I read the news item on p.6 of the AVSA March issue, regarding the Super Titan mains conditioner.
It says there that this unit can deliwer 9,2 KVA, with 35,5 KVA of transient power on tap. This would mean some 40A off a 230VAC supply, which either needs a special connector to mains or a 3-phase installation. If this is correct, I would have expected the agent to tell us so.
Is this correct, or is there a printing error?